Originally Posted by drcoffee
New data: Pulled relay and checked voltage of #3 on ground and solid at all rpm. Checked continuity of #4 on ground and at idle no resistance(0 ohms) but with increased rpm, resistance rose to 3 Ohms+. Does that mean the ground in the fuse box is faulty?
Around 3 Ohms is a fine ground, so no problem there. By the way, ground for relay socket 4 comes from the ECU. You may want to repeat the 3&4 voltage test to rule out user error.

*While I checked the above I put a gauge on the low side. at Idle it was 25#s, static it was 50#s, when I raised the rpm to 2000 rpm it went into vacuum. WTF! Is that an expansion valve or something else. It isn't normal, I know that much. Still blows cold air.
Was the cabin blower on high during this test?

And the static pressure seems too low. What is the outside temp where you are? For example, static pressure should be 88 psi at 80F (after high and low sides have equalized).
 

Last edited by RonJ; Jul 13, 2011 at 01:55 PM.
Old Jul 13, 2011 | 01:57 PM
  #22  
drcoffee's Avatar
Thread Starter
|
Junior Member
Joined: Jul 2011
Posts: 11
Default

Blower AC set to max fan speed. It's 75-80 here today. What would cause the low side to go into vacuum though. Should I toss in a can of freon?

Originally Posted by RonJ
Around 3 Ohms is a fine ground, so no problem there. By the way, ground for relay socket 4 comes from the ECU. You may want to repeat the 3&4 voltage test to rule out user error.
So does the ECU shut power off on accelleraton?
 

Last edited by drcoffee; Jul 13, 2011 at 01:59 PM.
Old Jul 13, 2011 | 02:21 PM
  #23  
RonJ's Avatar
Recognized HCF Member
Joined: Sep 2007
Posts: 9,453
From: Houston, Texas
Default

Originally Posted by drcoffee
Blower AC set to max fan speed. It's 75-80 here today. What would cause the low side to go into vacuum though. Should I toss in a can of freon?
The readings are confusing and inconsistent with the fact that the A/C blows cold. First, the static pressure reading is too low. Were the low and high sides equalized? You need a manifold gauge set to sort this out. Vacuum could indicate moisture in the system or a bad expansion valve.

So does the ECU shut power off on accelleraton?
No. But a tripped A/C pressure switch or thermostat would.
 
Old Jul 13, 2011 | 04:01 PM
  #24  
drcoffee's Avatar
Thread Starter
|
Junior Member
Joined: Jul 2011
Posts: 11
Default

So I just added 9oz of freon and it does not go into vacuum anymore but drops to about 5-10# as the engine rpm rises. It seems to be cooler than before but I'm going to have to check the expansion valve in a few days and see if its getting frosty. Where is that thing anyway?

Update: I turned off the engine and let the car stabilize for an hour. The static reading is now 105#. When I started the engine the low side dropped to 25# at idle and cycled normally with the fans on/off.
 

Last edited by drcoffee; Jul 13, 2011 at 04:12 PM.
Old Jul 13, 2011 | 04:08 PM
  #25  
RonJ's Avatar
Recognized HCF Member
Joined: Sep 2007
Posts: 9,453
From: Houston, Texas
Default

Stop adding refrigerant without readings from a manifold gauge set. You have no idea how much refrigerant is already in system or whether there is air in there. Can't help you if you ignore advice.
 
Old Jul 13, 2011 | 05:17 PM
  #26  
mk378's Avatar
Recognized HCF Member
Joined: Jun 2007
Posts: 10,023
Default

Those gauges built into the charging hose are accurate to about plus or minus 50 psi. Worthless.

If it gets cold once, you have enough refrigerant in the system. Either there is enough to make cold air, or there isn't. There aren't gremlins under the hood adding and removing it as you go down the road.

There is no pressure switch or control on the low pressure side. So watching only the low side pressure trying to think of why the compressor shuts down abnormally (if it even does) is useless.

Only high side pressure can cut off the compressor. The switch there is designed to be closed under all normal operating conditions (pressure from 50 to 400 psi). Normal compressor cycling is controlled by evaporator temperature.
 
Old Jul 13, 2011 | 05:27 PM
  #27  
drcoffee's Avatar
Thread Starter
|
Junior Member
Joined: Jul 2011
Posts: 11
Default

Originally Posted by mk378
Those gauges built into the charging hose are accurate to about plus or minus 50 psi. Worthless.
I think I'm using a fairly reliable gauge.

There must be a low side switch to keep the compressor from running when empty.

 
Old Jul 13, 2011 | 07:12 PM
  #28  
mk378's Avatar
Recognized HCF Member
Joined: Jun 2007
Posts: 10,023
Default

The high side switch has dual action, it is what will prevent the compressor from running when empty. It will be able to run with a very low charge though, which overheats the compressor, thus the use of a compressor thermal switch. There is no pressure switch on the low side.
 
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
Roentgen
Suspension, Brakes, Tires & Wheels
15
Sep 14, 2007 09:22 AM
89_slammed
ECU Tuning & Fuel Management
3
Mar 19, 2007 01:11 PM
Vexorg
Audio/Visual & Electronics
9
Apr 17, 2006 04:00 PM
sacicons
Vendor Group And Special Buys
14
Oct 23, 2005 10:05 PM
b16Ek4
Mechanical Problems & Technical Chat
3
Jun 20, 2005 10:59 PM




All times are GMT -8. The time now is 11:33 PM.